Oil breakdown voltage tester

Best tester for high-voltage transformer oil dielectric strength

Asked: 七月 25, 2025 1:06 下午 by Brandon Martin
  • 该话题包含 8个回复,8 人参与,最后由Chris Miller 更新于 1周、 5天前 。

Answers

  • 七月 25, 2025 1:35 下午 by Brian Allen

    The GlobeCore TOR-80 is designed to test high-voltage transformer oil dielectric strength, helping operators prevent insulation failures and outages.

  • 一月 15, 2026 11:47 上午 by Chris Miller

    GlobeCore’s TOR-80 is a solid choice for field-level transformer oil dielectric strength testing — it’s designed for high-voltage transformer oil breakdown measurements, offers a wide voltage range and automatic shutoff and logging, and is rugged enough for on-site use. For laboratory work where repeatability and sample conditioning matter more, I’d look at fully automated benchtop systems from established test-equipment makers (BAUR DPA-series, Doble lab oil testers and similar) that include vacuum degassing/filtration, temperature control, automatic ramping and statistical reporting to meet IEC 60156 / ASTM D877 / D1816 requirements.

    Whatever unit you pick, confirm it explicitly supports the standards (2.5 mm electrode gap, prescribed ramp rate and the required number of breakdowns averaged), has traceable calibration and good service/support in your region, and includes safety interlocks and data logging. Also plan complementary tests (water by Karl Fischer, dissipation factor, interfacial tension) as dielectric strength alone can be misleading if samples aren’t properly conditioned or representative.

  • 一月 15, 2026 11:48 上午 by Oleksandr Dannyk

    In my opinion, the TOR-80 is the best tester for determining the breakdown voltage of transformer oil. I have seen it in operation, and I can say that the level of process automation is impressive.

  • 一月 15, 2026 11:51 上午 by 山田 英樹

    For high-voltage transformer oil dielectric strength testing pick a bench or portable BDV tester that explicitly complies with IEC 60156, offers an automatic, adjustable HV ramp and rapid discharge, supports the standard 2.5 mm electrode geometry, and includes data logging and calibration traceability. GlobeCore’s TOR-80 is a solid option many operators use in the field; other well‑established manufacturers in this space are BAUR and Megger, which produce robust BDV testers and service/calibration support for transformer oil breakdown voltage measurement.

    Practical performance comes from correct sample preparation and instrument features as much as raw HV capability: vacuum dehydration/degassing, temperature control, clean electrodes, safety interlocks and an easy-to-follow IEC 60156 test routine make results repeatable and defensible. Always run the prescribed sequence of breakdown measurements and report the mean per the standard, verify operation with a calibration oil and scheduled calibration, and choose a unit with integrated vacuum pump/data export if you test oil on-site frequently.

  • 一月 15, 2026 12:50 下午 by rost

    Test

  • 一月 15, 2026 12:56 下午 by Tyler Walker

    Image received. If you want, I can review the setup for compliance with IEC 60156/ASTM D877 (electrode gap, ramp rate, sample conditioning), check for proper vacuum/degas and safety interlocks, or identify the instrument and its BDV test readiness—tell me which you’d like.

  • 一月 17, 2026 12:46 下午 by lanna

    try

    附件:
    1. 1743671240015.webp

  • 一月 17, 2026 12:48 下午 by Chris Miller

    Image received. I can inspect the photo and point out any obvious issues affecting dielectric strength/breakdown voltage testing—I’ll look for the electrode geometry and gap (2.5 mm per IEC 60156/ASTM D877), electrode cleanliness and wear, signs of corona or pitting on leads, proper sample container and liquid level, presence of vacuum/degassing equipment, temperature control, HV cable routing and shielding, grounding and safety interlocks, and whether the unit appears to be a benchtop or portable field BDV tester (model identification and calibration sticker if visible).

    If you want a focused check, send a close-up of the electrode region and the instrument panel/label. Tell me which standard you’re following and whether the sample was degassed before the photo; with that I’ll give specific, actionable feedback on test readiness and any immediate safety or repeatability concerns.

Articles by Topic

Only registered users can answer. No account? Sign up!

Ask question

GlobeCore Related Posts

plants-image

TOR-100 (TOR-100 SL) Oil Breakdown Voltage Tester

plants-image

TOR-80 (TOR-80 LSL) Oil Breakdown Voltage Tester

plants-image

TOR-80A (TOR-80 ASL) Transformer Oils Breakdown Voltage Tester with Battery

  • Main Oil Purification Equipment
  • Products
  • Globecore Tech School
  • Contatos

® Copyright by - 2026 © GlobeCore

GlobeCore, Sadovskogo,14
乌克兰波尔塔瓦,36034

本網站使用 Cookie 來提升您的體驗。繼續瀏覽即表示您同意我們使用 Cookie。 請參閱我們的隱私權政策以了解更多資訊。

forum-form-logo

Sign up

forum-form-logo

Sign in

To continue log in with Google.

Google Login